Well I had a guy randomly drive through and we had a long chat. Apparently the guy who maintained this many years ago used whatever material was handy; the basement bears this out. There's galvanized screwed into black iron, PVC, some other unidentified plastic, not a vent in sight. Random bits of copper pipe connecting to galvanized and plastic for supply.3" tee at the bottom needs to be a combo. Rubber fernco coupling needs to be a shielded coupling. Shower needs its own vent, you could use an AAV if codes allow. Shower tailpiece is too long, trap needs to be raised up. Kitchen should have a trap above floor in the cabinet, if that's the case remove the kitchen trap in the picture. AAV needs to be minimum 6" above the trap arm of the fixture it serves. Horizontal to vertical transitions need to be done with a santee. Vertical to horizontal needs to be a combo.
How many times has the shower drain been replaced? Lol.