1" Rolled copper tubing leak underground patching?

Plumbing Forums

Help Support Plumbing Forums:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Rapidrob

Member
Joined
Jun 17, 2019
Messages
18
Reaction score
1
Location
Albuquerque
My water main is 1" Rolled Copper Tubing that is 125 yards long. I noticed my water bill was higher than normal and knew I had a leak somewhere in the run of tubing. I live in the desert so normally any water leaks will be shown by green plants growing very happily. This is not the case.
After two months of leaking I noticed the basement wall was wet through a small crack in the foundation. This has never happened in 31 years.
I assumed the leak was on the outside wall of the basement foundation and did an educated guess as to where it may be. As it turned out I was only a few feet off from the leak as a trickle of water was slowly flowing to the right of my hole in the ground.. The main shut off is 125 yards away and I have the tools to do so. Not a fun job when in you 70's.
My question is that the 1" rolled copper tubing is not the same size (OD and ID) as "normal" copper pipe is. When I uncover the leak, I'm not sure what will be needed to repair the leak? Once the leak is uncovered I'm sure it will be impressive and I will have to shut off the main. If the repair parts are not common, I'll be out of water until I can order them which will take several days to show up. I have soldering skills and have done repairs in the past on normal copper tubing pipe. I just installed two Ball Valves in the water main inside of the house. I can now isolate the outside water line for draining as the line is lower than my basement sink. I'm not sure if I can drain the line before the leak running the 125 yards to the water meter/shut-off. There is a slight uphill to my home.
Thank you for any helpful info.
 
Rolled copper soft tube tends to not be round enough to allow fittings to work properly...so, we have in our arsenal "shaping" tools for copper. Though, the tools are for standard sized copper tubing, 1" or 1-1/4" etc. The O.D. of tubing is uniform whether L or K type copper tube.
Most good plumbers these days have ProPress or "press" fittings and without fully draining whatsoever.
Note: soft copper tube is not suitable for press fittings over 1-1/4"
 
The water line is 3 feet down
I'll look into press fittings.
I plan on uncovering the leaking tubing today and see what I'm up against.
Thank you for the info.
 
Have you looked into a "Dresser" repair clamp? Get the real Dresser, not the fake China look-alike. That is nice; they will let you use the copper clamp tool.
 
I spent 8 hours digging the hole to the leak. The pipe is 4 feet underground and not copper. Somewhere a transition took place and the water line is 2.1" Black ABS plastic pipe. There was a large rock on the pipe and a 3/4" crack on its top surface.
The "trench" is only 1 foot wide and I cannot get to the pipe to clear and cut out the bad section and replace it.
I tried a Garlock rubber wrap and two radiator hose clamps but it did not work.
My neighbor has a small excavator and perhaps I can have him dig out the earth next to the pipe where I can get to it and do the repair.
My water pressure seems excessive. I'm going to contact my water company and have them check the pressure.
leak.jpg
 
Thank you! I'm not a plumber.
How do you repair poly pipe? I'm not seeing too many 2" fittings anywhere.
 