With a pressure gauge at the plate heat exchanger outlet , I am having a significant pressure drop between the combi and first floor shower head when there is a call for DW. The combi is on the first floor.The water pressure at the outlet of combi is 65 lbs static. With the pressure gauge at the combi, when the shower is turned on, the pressure drops to 30 lbs on the first floor for both hot and cold water. Then with the first floor turned off and the second floor shower turned on, water pressure at the combi is 47-50 lbs for the second floor. There is even a greater pressure drop if the first floor shower is turned on with the dishwasher at the same time; I get a low water condition.. The taps on both floors register 52 lbs at the combi when they are on. the spout and shower cartridge Moen 1222 have been replaced . The flow at the combi is 6gpm and the flow at the tub is 2.8 gpm. The pipe size is ¾” out of the combi to the ¾” thermostatic mixing valve and ½” to the shower valve. I don’t know what the pipe size is to the dish washer. Feedback please. Thank you and have a great day.