The Gas Company just arrived to my house. He laughed when I asked if he carried a manometer (which he did have with him), because he said they are now ancient. He said there are new crystal types available, but they are really expensive.
Getting back to the topic, he measured my gas and found 8.9 psi while flowing gas, and 9.5 PSI at standing pressure...all within normal limits. I explained the clogged air intake and he also believes this is what caused the fault because with natural gas being a constant pressure, which then mixes with a fresh air source, equals good combustion in the air/gas chamber. If you reduce the flow of air, the concentrate of gas increases, causing the gas pressure sensor to activate.
Does this sound plausible to the experts taking time to help me?
"Hello havasu",
I will not go into any further detail about Your Combustion Problem because You have already had some good Advice / Information from LiQuId - but just to comment on this point:
`The Gas Company just arrived to my house. He laughed when I asked if he carried a manometer (which he did have with him), because he said they are now ancient. He said there are new crystal types available, but they are really expensive`.
`Manometers are now Ancient` - ! !
It looks like here is another `Slight Difference` in attitudes regarding Gas Utilisation / Gas Pressure Measurement between the U.S. and the U.K.
Here in the U.K. the Professionals within the Gas Industry believe that there is NOTHING `Better` than the Manometer for Measuring Gas Pressures and Testing for Gas `Tightness` [No Leaks] on Gas Pipework.
Unless We are dealing with `Minute` tolerances of Gas Pressure - which would be beyond any Domestic Gas Appliance and MOST Light Commercial / Light Industrial Gas Appliances for Heating & Hot Water - there is NO Instrument that is better for Measuring Gas Pressures - Appliance Inlet Gas Pressure or Burner Pressure.
I / We have Combustion Performance Analysis Instruments / Multifunction Gas Measurement Instruments that Cost between $1100.00 [£700.00 approx.] and $1900.00 [£1200.00 approx.] - these have multiple facilities including the Measuring of Gas `Tightness` on Gas Pipework and Appliances and Measuring Gas Inlet and Burner Pressures on Gas Appliances - I / We would NOT even think about utilising any of these Instruments If We had a Manometer to hand - Which would ALWAYS be the case.
I am ONLY mentioning that I / We possess these `Combustion Performance Analysers` / Multifunction Gas Measurement Instruments to show that DESPITE owning perhaps $25,000 [£15,600 approx.] worth of these Instruments I / We would NEVER use one of them INSTEAD OF a Manometer.
When I / We are using a Combustion Performance Analyser the FIRST thing that We would do is to Measure the Gas Flow to the Gas Appliance - the Gas Inlet Pressure to the Appliance and the Burner Pressure - PRIOR to taking any Combustion Analysis Measurements - these Pressures are taken using a Manometer.
I would state Categorically that there is NO INSTRUMENT in existence that is `Better` for Checking & Setting Gas Pressures on Domestic / Light Commercial / Light Industrial Gas Appliances - Although of course the facility to Measure these Pressures CAN be utilised on the Multifunctional Gas Measurement Instruments that I have mentioned here.
Far from being `Ancient` - Manometers are a VITAL Measuring Tool for Gas Engineers / Gas Installers - Plumbers of course also use them.
I hope that this Post has NOT been `Too Boring` for the People who `Hate` My `Wall of Text` Posts.
Regards,
Chris