Hi,
I am trying to understand the California Plumbing Code section 906 on "Vent Termination".
https://up.codes/viewer/california/ca-plumbing-code-2022/chapter/9/vents#9
1. Does the code require _every_ vent termination to extend above the roof (per 906.1) and hence prohibits termination through the sidewall?
2. What does the section 906.4 "outdoor installation" relate to?
I have a plan to extend the vent through the sidewall to meet the 10ft criteria above the ground and away from opening. This would terminate under eves (no soffit vents).
Looks like other build codes allow for it but not CPC?
Thanks,
Michal
I am trying to understand the California Plumbing Code section 906 on "Vent Termination".
https://up.codes/viewer/california/ca-plumbing-code-2022/chapter/9/vents#9
1. Does the code require _every_ vent termination to extend above the roof (per 906.1) and hence prohibits termination through the sidewall?
2. What does the section 906.4 "outdoor installation" relate to?
I have a plan to extend the vent through the sidewall to meet the 10ft criteria above the ground and away from opening. This would terminate under eves (no soffit vents).
Looks like other build codes allow for it but not CPC?
903.1.4 Sidewall vent terminal.
Vent terminals extending through the wall shall terminate not less than 10 feet (3048 mm) from the lot line and 10 feet (3048 mm) above the highest adjacent grade within 10 feet (3048 mm) horizontally of the vent terminal. Vent terminals shall not terminate under the overhang of a structure with soffit vents. Sidewall vent terminals shall be protected to prevent birds and rodents from entering or blocking the vent opening.Thanks,