well **** I did not think about the other wall where the toilet is... and I am being serious. .. I was so stuck on making that other side right I missed the other wall I can go up. When going vertical on this vent should I use a sweep or a sanitary tee? or the one with a sweep going both waysThe only way to dry vent the toilet per code in a UPC environment is to have the vent within 6 feet of the toilet, and have that vent come off the line vertically of no more than 45 degrees off vertical until you reach at least 6" above the flood rim of the toilet.
So, unless you can install the heel 90 going down the stack and run the dry vent up at no less than a 45-degree angle until you are 6" above the flood rim of the toilet to miss the window, you are in the same predicament you are now.
Does there happen to be a wall between the toilet and the tub where you can run the dry vent vertically up from the drain line and that would be within 6' of the toilet?
If not, you could ask for a variance from your jurisdiction. If this was under the IPC code, your vent for the shower would properly wet vent the toilet, and you wouldn't even need the vent in question. The reason for a dry vent not being flat before it is above the flood rim of the toilet is because it may become blocked when a stoppage happens downstream of the vent. Even that happens here, the toilet will be physically wet vented by the shower vent. As such, I would think that the inspector would allow the dry vent in this case, but that is totally up to them.