Running into issues with the existing framing.
I changed the Lav vent from 1-1/2" to 1-1/4 because of framing space. This is OK
under the IPC; however, I also want to use it to wet vent the shower drain.
Thoughts on this?
    58 KB
It’ll work, I don’t know if your local code would allow it.
Wouldn't it meet the wet vent criteria?
I’ve never used a 1.25” pipe ever in a vent system. It might meet the code, Im not sure.
You’re actually not wet venting through the 1.25”. That’s being done in the 1.5”.
The 1.5" drains into a 2" for the shower. and a 1.25" would work for that also.
I just looked up the IPC code.
A lavatory is 1 DFU
The minimum size vertical wet vent is 1.5” with a max DFU of 1.
So yes, it’s legal.
The 1.25” vent is not a wet vent.