A tankless water heater may make sense if you have a need for unlimited hot water or if space is a huge concern. But I see them mostly marketed as a "green" alternative to traditional tank-style water heaters, the idea being that they don't waste energy in stand-by losses, that is, heat lost into the environment through the walls of that big tank of hot water.
So I decided to check for myself, what the standby loss would be from a typical (i.e. the one I'm probably going to buy) "energy saver" electric resistance water heater: the Bradford-White model M-2-40L6DS. This unit is 24" in diameter and 32" high. It is covered with 2" of insulation with an R-value of 16. The surface area of the water heater is about 23 sq-ft. If we assume the thermostat is set at 120 degrees, and it's sitting in a room at 70 degrees, the temperature differential is 50 degrees. Since R-value is sq-ft*degrees/(btu/hour), the heat loss through the water heater jacket is 23*50/16 = 72 btu/hour, which is 21 watts. That's right. The amount of energy you're saving by installing that expensive, trouble-prone, maintenance-requiring tankless unit is equivalent to one typical CFL light bulb.
Meanwhile, the energy lost in the hot water that's sitting in your pipes after you turn the faucet off, is estimated at 15-20% of your hot-water usage. So far greater energy savings can be achieved by minimizing the piping distance between faucets and hot-water heater. And if you're still concerned about the electricity usage, take the $1000-2000 you're saving by going with an inexpensive water heater, and put it towards a solar electric system.
So I decided to check for myself, what the standby loss would be from a typical (i.e. the one I'm probably going to buy) "energy saver" electric resistance water heater: the Bradford-White model M-2-40L6DS. This unit is 24" in diameter and 32" high. It is covered with 2" of insulation with an R-value of 16. The surface area of the water heater is about 23 sq-ft. If we assume the thermostat is set at 120 degrees, and it's sitting in a room at 70 degrees, the temperature differential is 50 degrees. Since R-value is sq-ft*degrees/(btu/hour), the heat loss through the water heater jacket is 23*50/16 = 72 btu/hour, which is 21 watts. That's right. The amount of energy you're saving by installing that expensive, trouble-prone, maintenance-requiring tankless unit is equivalent to one typical CFL light bulb.
Meanwhile, the energy lost in the hot water that's sitting in your pipes after you turn the faucet off, is estimated at 15-20% of your hot-water usage. So far greater energy savings can be achieved by minimizing the piping distance between faucets and hot-water heater. And if you're still concerned about the electricity usage, take the $1000-2000 you're saving by going with an inexpensive water heater, and put it towards a solar electric system.