claytoncarney
New Member
First attempt calculating water supply size.
Background:
Continually dropping flow rates (likely due to corrosion/hard water scaling) suggest replacing all building plumbing. Currently considering pex-a.
Looking at UPC Table 610.4, I see two entries which might be applicable:
Questions:
I ask because initial WSFU calculations (using 75% rule) indicate a 3/4" building supply is inadequate (Hot 9.375 FU and Cold 15.875 FU, totaling 25.25 FU for the building supply).
Background:
- Single story family residence
- Built in 1955
- All building piping is 1/2" galvanized steel
- 3/4" meter/service
- Meter located 40' from building, 3' below floor level
- Static pressure at floor level is 65 psi
- Supply line from meter to building replaced with 3/4" pex-a 5 years ago
Continually dropping flow rates (likely due to corrosion/hard water scaling) suggest replacing all building plumbing. Currently considering pex-a.
Looking at UPC Table 610.4, I see two entries which might be applicable:
- 3/4" meter/service and 3/4" building supply
- 3/4" meter/service and 1" building supply
Questions:
- Am I interrupting the table correctly: can you connect a 1" building supply to a 3/4" meter?
- If so, would it make sense to use a 1" building supply when the line between the meter and the building is only 3/4"?
I ask because initial WSFU calculations (using 75% rule) indicate a 3/4" building supply is inadequate (Hot 9.375 FU and Cold 15.875 FU, totaling 25.25 FU for the building supply).