There are two places to connect a manometer. There’s a screw on the gas inlet. Remove the screw and push a hose over where the screw was.
Inside the unit on the gas manifold there’s another screw. Same deal as above.
You shouldn’t mess with the inside port unless rinnai is advising you on what to be checking for.
Thanks. I probably should have looked under the unit for the big inlet port with the red tape next to it marked GAS and the obvious screw on a nipple.
So, I've got plenty of gas pressure.
Static pressure with nothing in the house using more than a pilot light amount is a steady 7.3-7.4 inches of water column. If the furnace is running full boar, it drops to about 6.8" (surprising; I had thought the furnace would eat more gas).
With just the Rinnai running (no furnace), with a light load such as slugging water through the recirc lines, it's down to about 6.9-7."0. With a heavy load of about 3 GPM from the hot taps (it's rare I would draw more than this), pressure drops to about 6.15".
Furnace heating plus heavy load of hot water flow takes me down to no lower than 5.2"; I left the water heater and furnace on together for a while and saw the pressure go up and down a bit (variance of about .2 to .3). But never lower than 5.2.
Spec for the unit is 3.5" - 10.5" natural gas, so there's no condition I'm running that would even get close to the lower limit. So, good news is I don't need expensive pipe rework (and, if a service guy tries to sell me pipes, I can send him packing). Bad news I still don't have an obvious culprit.
I appreciate the help. The Rinnai folks will likely have me check enough gas at the burner in case any regulator adjustments are needed in the unit; I see the plug on the case that's removable to access that, I think. But there's nothing for me to poke at meantime.