What would happen if when pressure testing a residential house you did not close off the shut off valves and instead pumped air directly at the gas valves for water heater/furnaces? Is it possible to damage the unit
Yes, you can blow the gas control diaphragms out.What would happen if when pressure testing a residential house you did not close off the shut off valves and instead pumped air directly at the gas valves for water heater/furnaces? Is it possible to damage the unit
Hello, our test is 50 ounces for thirty minutes . The gas was shut off from national fuel for a leak. Would this potentially do damage at this pressure ?Yes, you can blow the gas control diaphragms out.
How much pressure did you use ?
When appliances are left connected and I want to test an existing system, I pump the lines up with a bicycle pump to 8”-15” water column and watch my gauge for 15 minutes. If no pressure drop I call it good.
I also test sometimes with nitrogen and a digital manometer. It’s much more sensitive and you can check the system for tightness in just a couple minutes.
So would it potentially ruin the appliance if I did not shut the valve off at that pressure? National fuel didnt seem to think so at all and it's throwing me a big curve ball. A co worker of mine said the same thing where you can test up to the fixture with this pressure but I was told diffrentWhen I test with higher than working pressure I disconnect the appliance and cap the supply outlet. This way if the valve leaks it doesn’t ruin your gas control of the appliance.
It could potentially damage a gas control. That’s roughly 3psi.So would it potentially ruin the appliance if I did not shut the valve off at that pressure? National fuel didnt seem to think so at all and it's throwing me a big curve ball. A co worker of mine said the same thing where you can test up to the fixture with this pressure but I was told diffrent
Appreciate it , thank you sir. Was a big thing with national fuel in our area because they seem to not do it at all and it caused alot of drama between me and the customer in regards to me capping off the fire place and leaving sections unfully tested because the valves were further back leaving a bit more pipe untested.It could potentially damage a gas control. That’s roughly 3psi.
In that case IAppreciate it , thank you sir. Was a big thing with national fuel in our area because they seem to not do it at all and it caused alot of drama between me and the customer in regards to me capping off the fire place and leaving sections unfully tested because the valves were further back leaving a bit more pipe untested.
Everything from it simply not working properly to starting a fire when the valve malfunctions. Gas leaks…..etc.Any idea what would happen that would be noticeable to a homeowner in the event of the pressure affecting it ?
If your meter regulator blows out and your system sees 50psi street pressure then you don’t have to worry about your pipe leaking…….your appliances will leak and your house will probably blow up.Great idea to pressure test your gas lines! But the key word is “LINES”. Not the appliances. Most appliances will say something like “1/2 PSI MAX”. So disconnect the appliances, cap them off or use a shut off valve such that you’re only testing the delivery lines.
In my case, I piped the house with 1-1/4” main line and 1” lines branched out from there. I made an adapter that had a 1/4” npt and a dial pressure indicator to monitor. Using a small air compressor, I pumped the system up to 50 psig. Why ‘so high’? Because the street Natural Gas source is around 40-45 psig, so if my gas meter or regulator FAILS OPEN, the house will see all of that! So, . . . test for it.
Back to my method; with a static 50 and a dial gauge verifying it, I sprayed every joint with leak indicator and verified at least twice. An hour or more later, came back to the dial indicator to check if it moved.
By this time, the Gas Co inspector showed up (by appointment) and checked my setup. He said they don’t go to “This level of testing, and know of ant contractor either”.
For good measure, after the house was operational, I used a gas ‘sniffer’ to detect anything, both on the first day and a week later.