notsure1976
Member
My wife wanted a gas range, how many posts here start with that? So, I bought one (when both our Kenmore/LG fridge and Samsung washer died in the same week). You know the type of week I am having...
We had an extra natural gas hookup in the basement that could be rotated 90 degrees to be exactly where I needed it upstairs. Awesome! Then I decided to check to be sure that the gas pipe in my house, which was built in 2004, was sized appropriately to handle this large range....
I looked in the home-flex book for CSST installations and according to that chart (7.11), using the long run method, my main supply and dryer where fine. However, the new range, furnace, and hot water heater should all be on 3/4" and not 1/2" lines. Yet, the furnace was tagged as passing inspection--this requirement would be the same regardless of my range. Hmmmm.
http://www.valenciapipe.com/product-downloads/home-flex-csst/HOME-FLEX_Installation_Manual.pdf
Then I consulted the IFGC manual. According to this my main line might even be too small! Yikes. http://publicecodes.cyberregs.com/icod/ifgc/2009/icod_ifgc_2009_4_par013.htm
The problem I am having with figuring out the right answer is deciding which pipe sizing chart to actually use. This depends on the nature of the natural gas that is coming into the house. On the meter is says that I have 5psig with 1/2 diff. but the regulator on the meter has a 1/8 orifice and is at 7wc.
My guess is that 7wc is about 1/4 psi and I should be using a low pressure sizing chart. However, I could be wrong.
I have attached a drawing. Can someone PLEASE look at this and tell me what chart to use and what sizes need to change? I think I need to buy a lots of 3/4 CSST! (SEE ATTACHED PICTURE FOR MY CURRENT SETUP)
We had an extra natural gas hookup in the basement that could be rotated 90 degrees to be exactly where I needed it upstairs. Awesome! Then I decided to check to be sure that the gas pipe in my house, which was built in 2004, was sized appropriately to handle this large range....
I looked in the home-flex book for CSST installations and according to that chart (7.11), using the long run method, my main supply and dryer where fine. However, the new range, furnace, and hot water heater should all be on 3/4" and not 1/2" lines. Yet, the furnace was tagged as passing inspection--this requirement would be the same regardless of my range. Hmmmm.
http://www.valenciapipe.com/product-downloads/home-flex-csst/HOME-FLEX_Installation_Manual.pdf
Then I consulted the IFGC manual. According to this my main line might even be too small! Yikes. http://publicecodes.cyberregs.com/icod/ifgc/2009/icod_ifgc_2009_4_par013.htm
The problem I am having with figuring out the right answer is deciding which pipe sizing chart to actually use. This depends on the nature of the natural gas that is coming into the house. On the meter is says that I have 5psig with 1/2 diff. but the regulator on the meter has a 1/8 orifice and is at 7wc.
My guess is that 7wc is about 1/4 psi and I should be using a low pressure sizing chart. However, I could be wrong.
I have attached a drawing. Can someone PLEASE look at this and tell me what chart to use and what sizes need to change? I think I need to buy a lots of 3/4 CSST! (SEE ATTACHED PICTURE FOR MY CURRENT SETUP)