I have to run a water main that's 1500' long with 250' in elevation gain with 180 psi at the meter. I was told by a septic tank guy wanting to run the water line that I'll need a 1" meter and 1" pipe with 3 pumps to have any pressure. I'm not wanting to deal with pumps at all. My local water co. said a 3/4" meter with 1" pipe and no pumps will be plenty. My options for meters are 3/4" $1800, 1" $3100 and 2" $5000. I'm planning on doing myself with HDPE. Also can I run two HDPE lines touching in the same trench or with they wear on each other?
 
the simple science is that you loose .433 lb of pressure for each foot of elevation change ...so that puts you at a static loss of 105 psi, leaving you 75 psi.
UPC chart only goes to 1,000 ft, and shows at over 60 pressure range, a 3/4" meter and 1" pipe gives you enough pressure for 11 fixture units and with 1-1/4" pipe, 21 f.u.
11 fixture units would break down to 1 10 f.u. tub/shower and one lav. no improvement with a 1" meter.
at 1,500', fugedaboutit without a pressure boost system.
Have an engineer design it unless you have a damn reliable plumbing contractor.
 