In my line of work it means Flow Line Which would be the bottom of the pipe. Spring line is halfway up the pipe. From that drawing it looks as if the guy who drew it meant Flow line but I could be wrong.
It looks as if you have a 6" Sewer lateral coming of a a SMH (Sewer Manhole) (most homes are 4" not 6" so I would question that). According to the plan they want you to do a 6" cut in Wye with a 6" x 4" Bushing and then a 4" x 1-1/2" Bushing and run the 1-1/2" Solvent weld pipe. Along witht he wye they are requiring a new 6" Clean out, How I read this is that the existing line is 4.2' deep to flow line (Where the tie in is being done) and the 4" Cast Iron stub out of the house is at a cut of 2.7' deep to flow line. ( if there is a pump that would mean there is reverse flow so there is a manhole of some sort with a pump in it and I would assume the outlet of that is the cut of 2.7'. From what I read you have a fall of 1.5' (18")in 58 feet of pipe so you have a fall of .31 inches per foot which is greater then 2% which is fine.