Gents,
Lil issue I am having with my gas HW Tank. I have noticed some slight dripping coming from relief valve. I installed a new expansion tank at the same time of replacing HW tank 2 years ago. I just checked my static pressure and here are all my readings.
Static Pressure 100psi
running pressure 58psi
Expansion tank 98psi
I tried to lower (adjust) Back Pressure Regulator however my static pressure did not change.
I recently pumped air into expansion tank to 60psi when draining HWT and no water pressure was present.
I am an Electrician not a plumber so take it easy on me. From things I have read it seems I may have a bad Back Pressure Regulator. It is 13 years old. Is that the norm? Do you too think its the BPR? Also should expansion tank air pressure (prior to water pressure) be set the same as static water pressure? any advice is appreciated.
Lil issue I am having with my gas HW Tank. I have noticed some slight dripping coming from relief valve. I installed a new expansion tank at the same time of replacing HW tank 2 years ago. I just checked my static pressure and here are all my readings.
Static Pressure 100psi
running pressure 58psi
Expansion tank 98psi
I tried to lower (adjust) Back Pressure Regulator however my static pressure did not change.
I recently pumped air into expansion tank to 60psi when draining HWT and no water pressure was present.
I am an Electrician not a plumber so take it easy on me. From things I have read it seems I may have a bad Back Pressure Regulator. It is 13 years old. Is that the norm? Do you too think its the BPR? Also should expansion tank air pressure (prior to water pressure) be set the same as static water pressure? any advice is appreciated.