The idea is to treat everything 6” above the flood level rim and below as drainage and everything above as the vent system.
So the vent system would be the only exception where a sanitary tee could be laid down. In the drainage system it can only be allowed to stand up.
If the piping has the possibility to be flooded at any point, like a blockage in the system, then it’s considered the drainage system even if it’s a dry vent.
It’s similar to the rule about a flat vent below the floood level rim that’s not washed by a fixture, it’s not allowed because solids can back up into that portion and block the vent. They want you 45 degrees or more to be considered vertical but you still have to use long sweep fittings
It’s been said The sweep of a sanitary tee on its back isn’t great enough to allow the pipe to clear itself of solids when in a vertical position.
This could be a problem in a revented situation where you had no access to clear the vent.
Drain cables do not like making the transition from vertical to horizontal through a san tee on its back, this is especially true with 3”-4” pipe.
I’m not saying I agree with all of this, I’m just trying to give an explanation as to why it’s not legal to do in all jurisdictions.
The only way I lay San tees down is when I have no room for long sweep fittings and it would weaken the structure to make them fit without expensive structural work. But I always make provisions for great cleanout access when I do. Rare occasions.
So the vent system would be the only exception where a sanitary tee could be laid down. In the drainage system it can only be allowed to stand up.
If the piping has the possibility to be flooded at any point, like a blockage in the system, then it’s considered the drainage system even if it’s a dry vent.
It’s similar to the rule about a flat vent below the floood level rim that’s not washed by a fixture, it’s not allowed because solids can back up into that portion and block the vent. They want you 45 degrees or more to be considered vertical but you still have to use long sweep fittings
It’s been said The sweep of a sanitary tee on its back isn’t great enough to allow the pipe to clear itself of solids when in a vertical position.
This could be a problem in a revented situation where you had no access to clear the vent.
Drain cables do not like making the transition from vertical to horizontal through a san tee on its back, this is especially true with 3”-4” pipe.
I’m not saying I agree with all of this, I’m just trying to give an explanation as to why it’s not legal to do in all jurisdictions.
The only way I lay San tees down is when I have no room for long sweep fittings and it would weaken the structure to make them fit without expensive structural work. But I always make provisions for great cleanout access when I do. Rare occasions.