C CaliforniaPlumbing New Member Joined Nov 8, 2021 Messages 4 Reaction score 0 Location San Diego Nov 8, 2021 #1 Floor Drain + Laundry Drain connected by a 90 & Wye. All 2" inc vent. Would this pass inspection? Thank you Last edited by a moderator: Nov 8, 2021
Floor Drain + Laundry Drain connected by a 90 & Wye. All 2" inc vent. Would this pass inspection? Thank you
T Twowaxhack Currently in the Lab conducting research Professional Joined Feb 9, 2021 Messages 14,947 Reaction score 7,127 Location United states Nov 8, 2021 #2 It wouldn’t pass here and I doubt it would in California. You have a major fixture over a minor. The floor drain needs to be vented.
It wouldn’t pass here and I doubt it would in California. You have a major fixture over a minor. The floor drain needs to be vented.
C CaliforniaPlumbing New Member Joined Nov 8, 2021 Messages 4 Reaction score 0 Location San Diego Nov 8, 2021 #3 Wet vent not allowed here?
T Twowaxhack Currently in the Lab conducting research Professional Joined Feb 9, 2021 Messages 14,947 Reaction score 7,127 Location United states Nov 8, 2021 #4 CaliforniaPlumbing said: Wet vent not allowed here? Click to expand... Sure they are but you can’t put just any fixture above and wet vent through it. A washing machine is a high flow fixture.
CaliforniaPlumbing said: Wet vent not allowed here? Click to expand... Sure they are but you can’t put just any fixture above and wet vent through it. A washing machine is a high flow fixture.
CT18 professional Professional Supporting Member Joined Apr 30, 2014 Messages 1,380 Reaction score 566 Location Bloomfield Hills, Michigan Nov 9, 2021 #5 What Two said, you can wash it with a lav if your code allows wet vent
ReelPlumber Professional Professional Joined Jan 22, 2011 Messages 20 Reaction score 13 Location Orlando, Florida Nov 25, 2021 #6 This should make that legal. I would still be concerned about suds backing up out of floor drain.
M MrInfoPhilly Professional Professional Supporting Member Joined Jan 15, 2022 Messages 233 Reaction score 53 Location Earth Feb 3, 2022 #7 Isn't there something about 12ft for suds in the code distance wise... tired