Brief backdraft at the water heater when when inducer motor starts until main burners ignite then fine

Plumbing Forums

Help Support Plumbing Forums:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Maface

Member
Joined
Jan 6, 2023
Messages
5
Reaction score
1
I had a new 80% gas furnace installed which shared a common flue up thru the roof. the old furnace was naturally vented without a draft inducer. Now when the draft inducer kicks on there is a brief backdraft at the top of the water heater until the main burner fires, then it draws well. on the water heater there is a vertical pipe leading to a slowly angled up horizontal run to the main B stack. I wonder if increasing the angle or placing a small piece of sheet metal angled up where the water heater flue enters the B stack to prevent the inducer draft motor from blowing towards the water heater would help. Thank you for advice.
 

Attachments

  • 1673063193809.png
    1673063193809.png
    612 KB
  • 1673063214330.png
    1673063214330.png
    577.9 KB
The furnace needs to tie in above the water heater flue. The furnace flue is fan assist and is creating positive pressure and causing a backdraft through the water heater flue. I would swap the connections so that the furnace is on top.
 