Hello. I just had a water recirculation pump installed but I'm not sure it's correct. The end point takes about 2 minutes to get hot water so the pump was installed to fix that. It's still taking a while to get hot water so I'm not sure it's correct. Can you see any big issues with this? Thank you1000000757.jpg1000000758.jpg1000000759.jpg
 
  1. There must be a hose bibb at the bottom of the tank to allow draining so FAIL there.
  2. For a pump to do anything there needs to be a dedicated return line or
  3. a bridge ("Grundfos bridge") at the far fixture and in that case the entire job is a failure anyway.
  4. we always put isolation and bleed tees on both sides of the pump
no professional trained in plumbing did that and they should be schooled before going out into the field.
NOTHING WITH THIS IS RIGHT
 
Last edited:
What a mess! The pictures seem to indicate that this installation is taking suction from the bottom of the water heater and pumping it into the cold-water inlet of the water heater. Is that what I'm seeing????
 
  1. For a pump to do anything there needs to be a dedicated return line or
  2. a bridge ("Grundfos bridge") at the far fixture and in that case the entire job is a failure anyway.
Hahaha, I didn't even notice that until you mentioned it....I must say it is doing a fine job circulating the water heater....
 