Toilet vent min. Is 2" however you need a full size cleanout before you can reduce to 2" if this is a second floor application you could flat vent a toilet with 2". cleanouts are not required on second floors (residential). and no 3" will not fit in 2 x 4 wall unless its steel stud.
The only way I would wet vent a toilet would be on a conventional set up. With a 3 x 1/2 san tee arming over for the lav then reducing after the santee to 2" and vtr.... plumbing and I have a love hate relationship.
Ive done a lot of messed up plumbing then :/
johnjh2o said:Do you under stand the reasoning behind not running a flat un-washed vent below the flood rim? What could also happen with that setup is if there was a stoppage in the main line it could plug the vent and there would be no way to clear it.
John
That makes sense but the vent would get a cleanout any to test vent system.
johnjh2o said:I've got the time, I'm retired. How long have you been doing plumbing? I to look back at some of the things I did when starting out that I'm not proud of. It's all part of the learning process.
John
desertwater said:That makes sense but the vent would get a cleanout any to test vent system.