Rinnai RUR199 lower flow rate than expected

Plumbing Forums

Help Support Plumbing Forums:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Fromcarolina

New Member
Joined
Apr 13, 2022
Messages
1
Reaction score
0
Location
Durham, NC
I have a Rinnai RUR199eN which was installed in February. Since installation, I’ve wondered about the apparent low flow rate. I did some testing today.

I have at least 10.5 GPM on the cold side. It may be greater as the only way I had to measure was from two 1/2 hose bibs running at the same time. I’ll test at the Rinnai as soon as the 10 foot 3/4 hose I ordered arrives. However, pressure at the Rinnai would not be affected by anything in the house as it connects to the cold right where the main enters the crawl space.

I find that I only have 4.2 GPM as output flow rate (option 01 of Performance data at the Rinnai). Parameter setting 11 is at B - High. My cold water inlet temp is 61 degrees F at the coldest (performance data option 08). Hot water temp is set on the unit at 120 degrees F.

Having only a 4.2 GPM output flow rate does not make sense. With a set temp of 120 and inlet temp at 61 degrees, the Delta is 59 degrees. Looking at the Delta T chart, I should be getting a flow rate of about 7 GPM which would be satisfactory. Again, looking at the Delta T chart, an output flow rate of 4 GPM relates to a Delta of 95 degrees - meaning for the flow rate I am getting, my inlet temp would have to be closer to 25 degrees. This is a marked discrepancy and ridiculous.

Can anyone offer an explanation for this performance issue?
 
Make sure your water filter on the cold inlet is clean.

It’s black plastic and unscrews counterclockwise. Turn the water off and relieve the pressure before removing it.
 