when a house is built ,where does the relieve valve pipe [that goes into the wall] go to ???? i'm down in fl. and every thing is on a slab..
608.4 Each pressure relief valve shall be an
approved automatic type with drain, and each such
relief valve shall be set at a pressure of not more than
one hundred fifty (150) pounds per square inch (1035
kPa). No shutoff valve shall be installed between the
relief valve and the system or in the drain line.
608.5 Relief valves located inside a building shall be
provided with a drain, not smaller than the relief
valve outlet, of galvanized steel, hard-drawn copper
piping and fittings, CPVC, or listed relief valve drain
tube with fittings that will not reduce the internal
bore of the pipe or tubing (straight lengths as
opposed to coils) and shall extend from the valve to
the outside of the building, with the end of the pipe
not more than two (2) feet (610 mm) nor less than six
(6) inches (152 mm) above the ground or the flood
level of the area receiving the discharge and pointing
downward. Such drains may terminate at other
approved locations. Relief valve drains shall not
terminate in a buildings crawl space. No part of
such drain pipe shall be trapped or subject to
freezing. The terminal end of the drain pipe shall not
be threaded.
608.6 Any water-heating device connected to a
separate storage tank and having valves between
said heater and tank shall be provided with an
approved water pressure relief valve.
608.7 Vacuum Relief Valves. Where a hot-water
storage tank or an indirect water heater is located at
an elevation above the fixture outlets in the hotwater
system, a vacuum relief valve shall be installed
on the storage tank or heater.