N Nate848 Member Joined Apr 27, 2019 Messages 15 Reaction score 0 Location PA Jun 11, 2019 #1 I got everything set up and it seems to held 5psi for about 15 to 20 min then it dropped 1 to 1.5 psi after 30 mins. Should I worry about this at all or is it fine since it did not drop in the first 15 minutes? Thanks
I got everything set up and it seems to held 5psi for about 15 to 20 min then it dropped 1 to 1.5 psi after 30 mins. Should I worry about this at all or is it fine since it did not drop in the first 15 minutes? Thanks
B bbp Well-Known Member Joined Aug 19, 2018 Messages 107 Reaction score 36 Location Wisconsin Jun 11, 2019 #2 You have a leak. Can you fill with water?
N Nate848 Member Joined Apr 27, 2019 Messages 15 Reaction score 0 Location PA Jun 11, 2019 #3 yes but im afraid of the weight on the pipes. Its about 100 foot of 3inch and another 75 foot of 1.5 and 2inch.
yes but im afraid of the weight on the pipes. Its about 100 foot of 3inch and another 75 foot of 1.5 and 2inch.
frodo Just call me Macgyver Professional Supporting Member Joined Sep 28, 2014 Messages 8,578 Reaction score 2,977 Location right here right now, over there later on. Jun 12, 2019 #4 if the pipe will not hold the weight of a water test, it is not installed correctly pvs should be supported every 4' and on both sides of each fitting
if the pipe will not hold the weight of a water test, it is not installed correctly pvs should be supported every 4' and on both sides of each fitting
M Matt30 Professional Professional Joined Jan 16, 2012 Messages 2,319 Reaction score 923 Location Halifax, Nova Scotia Jun 12, 2019 #5 Where I plumb from, drainage pipes must hold a 3m column of water for 15 minutes. If the supports holding the piping will not support the weight of the pipes filled with water, it must be re done.
Where I plumb from, drainage pipes must hold a 3m column of water for 15 minutes. If the supports holding the piping will not support the weight of the pipes filled with water, it must be re done.