you are correct
1/2'' copper pipe at 40 psi only delivers 14 gallons per minute
3/4 delivers 26 gpm
3 terlets require 1.6 gpm = 4.6 gpm and you have other **** hooked up
5 sinks @ .8 per =4 gpm
2 showers @ 2.5 gpm= 5 gpm
1 tub @ =4
1 laundry machine =4
hose bib = 5 gpm
total is 26.6 gpm you need
a 3/4 pipe is 26 gpm
you need the 1''
bottom line. the 1/2'' is way way way undersized and needs to be removed
and repiped correctly
abandon the 1/2 '' line and repipe the system with a 1'' trunk
run 3/4 to the fixtures.
i guarantee your problem will disappear