What about not putting a 90° offset in the vent until we are above the flood level.
What about not putting a 90° offset in the vent until we are above the flood level.
What about not putting a 90° offset in the vent until we are above the flood level.
That wall is coming out. It is going to be an island cabinet.
How would propose to not offset until above flood rim?
you used a tee instead of a combo.
but what jumps out at me and screams...WTF!!!!!???
is the soldered copper joints instead of brazed joints.
Do you REALLY want to pull the cabinet in a few years, break the floor to fix a leak ?
your house, do as you wish, you been warned
after, you braze them. insulate the pipes to keep the concrete and rocks off of them.
copper contracts and swells with heat. if a rock is laying on the pipe, the movement will rub a hole in the pipe
concrete has lime in it, it will eat the pipe up
but what jumps out at me and screams...WTF!!!!!???
is the soldered copper joints instead of brazed joints.
Do you REALLY want to pull the cabinet in a few years, break the floor to fix a leak ?
your house, do as you wish, you been warned
after, you braze them. insulate the pipes to keep the concrete and rocks off of them.
copper contracts and swells with heat. if a rock is laying on the pipe, the movement will rub a hole in the pipe
concrete has lime in it, it will eat the pipe up
How is the different between solder or braze the copper joints? I need to talk to the guy again.
I need to know also...
Isn't there a need for a special coded copper pipe for use under concrete?
soft solder is a soft material, it will not stand up to the movement of the slab
oh yes, your slab moves. the ground moves also.
we braze the copper pipes, what fitting/connection material to use? I know the pipes should be L type. fittings shall be wrought copper, where can I buy this wrought copper?UPC, chapter 6 water distribution
609.3 Under Concrete Slab. Water piping installed
within a building and in or under a concrete floor slab resting
on the ground shall be installed in accordance with the
following requirements:
609.3.2 Copper tubing shall be installed without
joints where possible. Where joints are permitted, they
shall be brazed, and fittings shall be wrought copper.
Note: For the purpose of this section, “within the
building” shall mean within the fixed limits of the
building foundation.
609.4 Testing. Upon completion of a section or of
soft solder is a soft material, it will not stand up to the movement of the slab
oh yes, your slab moves. the ground moves also.