I installed iron gas pipe from the meter bar to inside the house and then from there I used csst and ran that to a stove. The fuel source will be natural gas and the meter has not been installed by the gas company yet
I pressurized the line to a little over 5 psi and had pressure loss. Identified 2 leaks and corrected them. Pressurized the whole system from end to end and the pressure held solid for more than 2 days. then it got cold out and the pressure in the line dropped from 5 to about 4.5 and then even colder today and the pressure has dropped down to 2 psi. I am not seeing any bubbles with a heavy soap and water spray at the joints, tees, and shutoffs.
Should the pressure start to dissapate over time naturally if just left there? Looking for some opinions as to what I am seeing .
5 psi at 46 degrees outside
4.5 psi at 35 degrees outside
2 psi at 30 degrees outside
thoughts please
I pressurized the line to a little over 5 psi and had pressure loss. Identified 2 leaks and corrected them. Pressurized the whole system from end to end and the pressure held solid for more than 2 days. then it got cold out and the pressure in the line dropped from 5 to about 4.5 and then even colder today and the pressure has dropped down to 2 psi. I am not seeing any bubbles with a heavy soap and water spray at the joints, tees, and shutoffs.