Improperly plumbed A/C condensate.

Plumbing Forums

Help Support Plumbing Forums:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Aggie83

Well-Known Member
Supporting Member
Joined
Jan 19, 2022
Messages
99
Reaction score
37
Location
Rising Star Texas
Moved into my newly-built home a little over one year ago. On Saturday night, we began smelling sewage and could not locate the source after much exploration, thinking maybe a vent pipe was cracked or lose. On Sunday, I called my plumber and he quickly solved the mystery: whoever plumbed the drainage for the central Air conditioner in the attic was an idiot. Wanted some other professional opinions before I call the building contractor and raise heck.

Both the regular condensate drain and the overflow drain empty into the stack for the bathrooms. The drain has a p-trap, followed by a ball valve. So, the p-trap kept the gasses out, until it dried out!!! I guess the ball valve it to block the trap from evaporating during winter, but wasn't told this. Also, where I live in Texas, the temparateres fluctuate 50 degrees F in one day often.... making crawling into the attic to flip a valve really stupid.

Also, since the overflow goes into the sewage system rather than outside the house how would you ever know the main drain was clogged? My wonderful plumber came out of the attic just pissed and I am also.

Tried searching plumbing codes and found nothing. Is this an acceptable way to plumb the drain pan?

Many thank,

Karen
 
No, that is not acceptable. Condensate line MUST have an air gap to enter a sewer line. Hard piped condensate lines into a sewer line are against the code. It will take me a minute to find it. That installation should not have passed an inspection.
 
I'm not sure what code you are under, but all codes should be similar on this issue. The appropriate IPC (International Plumbing Code) section is below.
1736260249088.png

Also, the secondary drain needs to discharge in a place that can indicate the primary drain is not functioning.
1736260426507.png
1736260480910.png
 
I'm not sure what code you are under, but all codes should be similar on this issue. The appropriate IPC (International Plumbing Code) section is below.
View attachment 47614

Also, the secondary drain needs to discharge in a place that can indicate the primary drain is not functioning.
View attachment 47615
View attachment 47616
For what it’s worth around here in North Carolina on new construction, it is not uncommon to have the primary air conditioner drain for an air conditioner in the attic drain with an air gap into the same drain stack used for the laundry. The secondary or emergency exits above a second floor window. The theory is that if you see water drip through your window you are supposed to understand something is not right, but very few people know this!
 