Model Select State Series 200/201 High Efficiency GS6 50 YOCT 2007 (This was in the house when we bought it 4 years ago, so I have no documentation)
Been having an issue where the pilot would go out after heating the tank, pretty much just like this guy.
http://www.plumbingforums.com/forum/f12/pilot-light-will-not-stay-lit-2883/
I have not opened the unit, but I did get in under the thing with compressed air and a feather duster and cleaned that filter. It worked for a day after that.
This morning it was out again, so I built a vacuum attachment consisting of a small piece of copper tubing and a shortened 90 so I could really get in there and vacuum the filter.
Problem now is the pilot wont stay lit. Tested the thermocouple and I am getting 25mw, so that should be fine.
Suggestions? Should I take it apart and clean out the burn chamber or is it possibly the valve?
Been having an issue where the pilot would go out after heating the tank, pretty much just like this guy.
http://www.plumbingforums.com/forum/f12/pilot-light-will-not-stay-lit-2883/
I have not opened the unit, but I did get in under the thing with compressed air and a feather duster and cleaned that filter. It worked for a day after that.
This morning it was out again, so I built a vacuum attachment consisting of a small piece of copper tubing and a shortened 90 so I could really get in there and vacuum the filter.
Problem now is the pilot wont stay lit. Tested the thermocouple and I am getting 25mw, so that should be fine.
Suggestions? Should I take it apart and clean out the burn chamber or is it possibly the valve?