Gehrkmania
Member
Hi guys - we've had an issue for several years with pressure building in our water system, especially after the water heater has been taxed (after showers, running the dishwasher, washing machine, etc.). After any of those events, when we first turn on any faucet - you can feel a stiffness in the movement of the handle and for the first couple of seconds, the water pressure is very high.
I think we need to install 1 or maybe 2 expansion tanks to keep the pressure from building after we use hot water.
We have a 50 gallon gas water heater. Because I am wildly overconfident, I bought an expansion tank before I bothered to check the pressure. I bought one of these from Amazon: Watts DET-5 2.1 G Potable Water Expansion Tank for 50-Gallon Water Heaters. It says it has a max pressure rating of 150 psi.
I just bought a pressure gauge and took some readings:
Street (taken at outside hose spigot nearest to the street) = 120 psi.
Inside, after pressure reducing valve (taken at washing machine cold water connection) - static pressure ~ 45 psi
Inside, same location after sitting overnight and having run dishwasher = 120 psi
I don't think we have a backflow preventer, so my assumption is that once the inside pressure goes above 120 psi, it's just pushing back into the line from the street and never rises above 120.
Is it as simple as adjusting the pressure in the expansion tank to match the static pressure in our system (~45psi), and then the tank will be able to absorb that extra 75 psi when the water heater gets in on the action?
Also - from what I've read, it sounds like we ought to be able to open up the pressure reducing valve a little and safely increase our static pressure by 15 or 20 psi. If that's the case, would there be any reason not to do that?
Thanks for your help!
I think we need to install 1 or maybe 2 expansion tanks to keep the pressure from building after we use hot water.
We have a 50 gallon gas water heater. Because I am wildly overconfident, I bought an expansion tank before I bothered to check the pressure. I bought one of these from Amazon: Watts DET-5 2.1 G Potable Water Expansion Tank for 50-Gallon Water Heaters. It says it has a max pressure rating of 150 psi.
I just bought a pressure gauge and took some readings:
Street (taken at outside hose spigot nearest to the street) = 120 psi.
Inside, after pressure reducing valve (taken at washing machine cold water connection) - static pressure ~ 45 psi
Inside, same location after sitting overnight and having run dishwasher = 120 psi
I don't think we have a backflow preventer, so my assumption is that once the inside pressure goes above 120 psi, it's just pushing back into the line from the street and never rises above 120.
Is it as simple as adjusting the pressure in the expansion tank to match the static pressure in our system (~45psi), and then the tank will be able to absorb that extra 75 psi when the water heater gets in on the action?
Also - from what I've read, it sounds like we ought to be able to open up the pressure reducing valve a little and safely increase our static pressure by 15 or 20 psi. If that's the case, would there be any reason not to do that?
Thanks for your help!