Hi all, my home uses a natural gas water boiler for radiant floor heating and I've been having a problem with low temperatures in the pipes. Sometimes it gets hot again after I try to drain air bubbles out of the pipes, but the problem keeps coming back.
There are two pumps (circulators) for the hot water going out of the boiler. The boiler is running fairly hot (about 140F as intended) and the water going through the first pump is also hot to the touch, but the water going through the second pump is not hot. The thermometer attached to the pipe out of the second pump reads 80F now, which is about 60F lower than the boiler's temperature after about 3 feet of piping -- I assume this is not normal, right?
I believe that the second pump was installed incorrectly by a family member because the manual says "Only install the pump with the motor shaft horizontal", but the shaft is vertical in our installation:
http://documentlibrary.xylemappliedwater.com/wp-content/blogs.dir/22/files/2012/07/P86203F.pdf
This video says the same as the above:
[ame]https://www.youtube.com/watch?v=UvrR5ZAkf10&feature=youtu.be&t=1m20s[/ame]
The following suggests that such orientation causes air bubbles to be trapped in the motor, which seems to fit with my symptoms:
[ame]https://www.youtube.com/watch?v=yiMECpYRByI&feature=youtu.be&t=2m17s[/ame]
I suspect trapped air in the pump is causing a lack of circulation, and the boiler may be getting turned on constantly which doesn't help -- this month my bill is 3 times more than last December (lol).
I am inclined to get a pump with the correct orientation or ask a plumber to cut the pipes and turn the pump flanges by 90 degrees. If I should get a new pump, I'm not sure how much GPM I need, but I suppose a stronger one is safer. Do you have some different suggestions? Sorry I don't know much but would appreciate some tips!
There are two pumps (circulators) for the hot water going out of the boiler. The boiler is running fairly hot (about 140F as intended) and the water going through the first pump is also hot to the touch, but the water going through the second pump is not hot. The thermometer attached to the pipe out of the second pump reads 80F now, which is about 60F lower than the boiler's temperature after about 3 feet of piping -- I assume this is not normal, right?
I believe that the second pump was installed incorrectly by a family member because the manual says "Only install the pump with the motor shaft horizontal", but the shaft is vertical in our installation:
http://documentlibrary.xylemappliedwater.com/wp-content/blogs.dir/22/files/2012/07/P86203F.pdf
This video says the same as the above:
[ame]https://www.youtube.com/watch?v=UvrR5ZAkf10&feature=youtu.be&t=1m20s[/ame]
The following suggests that such orientation causes air bubbles to be trapped in the motor, which seems to fit with my symptoms:
[ame]https://www.youtube.com/watch?v=yiMECpYRByI&feature=youtu.be&t=2m17s[/ame]
I suspect trapped air in the pump is causing a lack of circulation, and the boiler may be getting turned on constantly which doesn't help -- this month my bill is 3 times more than last December (lol).
I am inclined to get a pump with the correct orientation or ask a plumber to cut the pipes and turn the pump flanges by 90 degrees. If I should get a new pump, I'm not sure how much GPM I need, but I suppose a stronger one is safer. Do you have some different suggestions? Sorry I don't know much but would appreciate some tips!