this reminds me of my favorite episode of the Andy Griffith show, call your manufacture
Vent according to local authorities & unit manual specs. No Shortcuts (void warranty&call manufacturer)after all your nice work, sounds like u may have no choice but a chimney liner....
That boiler creates condensation in the flue gas you cannot use any metal venting and you cannot have it venting to a lined chimney it needs to be PVC all the way to the exterior of the house pitchedback towards the unit plain and simple done and done
this reminds me of my favorite episode of the Andy Griffith show, call your manufacture
Sounds like you could potentially remove the chimney, then use the framed chase. Start at the top and get rid of it.
Then make a simple run.
We do this sometimes but usually to get more room in the house. This assumes the flue is obsolete and abandoned.
Here in CA it is a seismic liability anyway, so there is a benefit to the effort and cost.
"The manual says that I can use all the common materials for venting"
What manual are you referring to? The Installation manual says, on P33, ONLY use (in USA):
PVC Sch 40 solid core
CPVC SCH 40 or 80
Approved Polypropylene
THERE IS NOTHING SAYING YOU CAN USE ALL THE COMMON MATERIALS.
Also read the" Measuring Vent Length" details about distance and elbows. Two 45 deg. elbows equals 3 linear ft of vent. 90 deg elbow equals 5 ft of vent. using 3"
I suggest you reread the installation instructions and have a licensed pro help you.
The Navien Warranty is "void" in the event of being "installed by a non-licensed installer." and or purchased from a supplier or distributor not authorized by Navien (which includes all e-commerce channels).
The bottom line is, if a 90% unit states PVC ,shortest distance, least elbows,and 12in. above min. Snowfall level with and 1/4 pitch per feet back towards the unit to drain condensation, all other sceneries, flue is most important, windy day, weather etc.
Your asking for problems....
I’ve installed many.....
80% furnaces were installed with chimney Liners or B vent do to sulfuric acid from combustibles in brick.
I’ve put put these units in closet, laundry rm, pantry. Wherever works best, u need minimal clearances.
2-45’s fittings equal to 1-90 minus 3-5 ft according to installations docs & termination according to mechanical code year your municipality uses (12”,18”, 24” 36” where ever your terminating near window, or above grade, be aware of snow drift, sometimes u have to check,
Stay 3 ft away from inside corner,
Because of back pressure
I have already said it,
you always run the vent then set the equipment 2 the vent
because of space restrictions and the bend rstrictions
start from the roof top with the vent, and install the vent
after you have installed the vent , move your boiler to match the vent
You got a lot of ideas on how to do this vent. I think at this point I would call the person that is going to inspect this and have
him come to your house and tell you exactly how he wants it done. Do it that way. Have him come back and inspect it, put the inspection
sticker with his name on the boiler and be done with it. You're ready for the winter.