We just installed our first Rheem ProTerra Hybrid Electric Water Heater (PROPH50 T2 RH375-30) and what a learning experience it was for us. We worked with an independent plumber that hadn't installed a hybrid before, didn't have the correct parts on hand and was clearly rushing to complete the job.
After showing these pictures to our Rheem rep he called out the following issues that we need to fix.
Thanks,
Shilo
After showing these pictures to our Rheem rep he called out the following issues that we need to fix.
- Condensate line should be CPVC or PVC with a Piping Tee to provide access opening for yearly inspection and cleaning (the plumber didn't put the garden hose in, he actually just left and that was all we could find to make sure condensate wasn't leaking out of the unit)
- Exhaust rotated so it’s free and clear of the wall
- No drip pan was installed
- Foam pad is only required on a concrete floor
- Expansion tank needs to be vertical or if horizontal it needs to be braced
- Need to get that black iron T off as it will rust and replace with brass T
- Seismic straps need to be anchored into the studs per code
- Would use flexible copper from the unit's cold water supply and hot water outlet and then finish the connection with whatever is preferred
Thanks,
Shilo