Hi, I'm adding two bathrooms to a 3-story house. I'm having difficulty finding a local company who can design & install the drain lines behind the wall. The ones I found on Yelp are almost only doing the service work fixing leaks and connecting of small fixtures.

Plumbing plays such an important role in the remodeling process. There are so many Qs need to be answered. How many stacks do I have (main line, # of branch lines)? What's the load on each stack? Can I add the new load to an existing drain stack, or do I need to branch off a new stack? How to lay the pipes to keep minimum disruption/drilling to studs & floor joists? Without seeing what's behind the wall and under the basement slab, how do I know the answers of those Qs above?

Is there such a designer role in a plumbing company that homeowners can consult with?

My two new bathrooms will contribute 15 DFUs total, one will bring in 5.5 DFUs (1 lavatory, 1 toilet, 1 shower), the other 9.5 DFUs (plus a standalone tub). The nearest stack has a current load of 22 DFUs, and it is ~38' away. The new bathroom floor is 1' elevated. The 38' distance will allow 9 1/2" drop (based on 1/4" per foot slope rate). Because the toilet flange and shower drain trap also take up space, I'm not sure if 1' difference will be enough. Can I do 1/8" slope rate if the pipe size is 3" or 4"? My water meter size is 1", street main has 144 psi, the most remote fixture is 109.5' away, highest fixture is 12.65' above water meter.

Can I connect them to this existing stack? A new branch stack is impossible to implement due to hydronic radiant floor. Could you please share what you think?

Thanks a lot!

Lily
 
I know the plumbing stack must have drain line in 3"~4" diameter. But which wall is the line behind? How to locate it behind the wall?
 
My two new bathrooms will contribute 15 DFUs total, one will bring in 5.5 DFUs (1 lavatory, 1 toilet, 1 shower), the other 9.5 DFUs (plus a standalone tub). The nearest stack has a current load of 22 DFUs, and it is ~38' away.

size pipe of nearest stack

size of pipe of existing sewer line
 
Last edited:
Ho Frodo, thank you very much for uploading the table and answering my Qs!

It looks like 3" pipe may be okay to handle my 37 DFUs, and my 38' distance will be okay because there is no limits on horizontal length. Am I right?
 
depends. on the building sewer size . if your sewer size is 3'' your shut down
if it is 4'' you are good to go

what concerns me is the 38' run and ceiling height
at the farthermost shower/ tub you will need a bare minimum of 9'' for the trap to fit
 