F Fiveoboy11 New Member Joined Dec 28, 2016 Messages 4 Reaction score 0 Location , Aug 14, 2017 #1 Essentially like for like but 40 gallon new vs 30 old. New ball valve, water connections and temp/pressure valve rigged up to go outside. Anyone see any problems? I'm in AZ.
Essentially like for like but 40 gallon new vs 30 old. New ball valve, water connections and temp/pressure valve rigged up to go outside. Anyone see any problems? I'm in AZ.
havasu Administrator Staff member Admin Joined Jan 5, 2010 Messages 13,021 Reaction score 3,912 Location Southern California, Aug 14, 2017 #2 Some will say a drip leg is needed for your gas line.
F Fiveoboy11 New Member Joined Dec 28, 2016 Messages 4 Reaction score 0 Location , Aug 15, 2017 #3 I checked and there is one back a bit, behind the shutoff valve Thanks for letting me know about that
I checked and there is one back a bit, behind the shutoff valve Thanks for letting me know about that
Mr_David Easily Amused Professional Joined Jan 11, 2010 Messages 4,170 Reaction score 1,061 Location Santee,Ca, Aug 15, 2017 #4 T&P relief drain can not go up hill. You can not use soft/annealed copper or any type of flexible tube. It has to drain downward. It can never ever be obstructed. The end should terminate outside or to an approved receptacle. Where does the t&p terminate? Last edited: Aug 15, 2017
T&P relief drain can not go up hill. You can not use soft/annealed copper or any type of flexible tube. It has to drain downward. It can never ever be obstructed. The end should terminate outside or to an approved receptacle. Where does the t&p terminate?
frodo Just call me Macgyver Professional Supporting Member Joined Sep 28, 2014 Messages 8,578 Reaction score 2,977 Location right here right now, over there later on. Aug 15, 2017 #5 .......... you need a pan and drain under the heater your relief valve is piped incorrectly the vent needs an offset
.......... you need a pan and drain under the heater your relief valve is piped incorrectly the vent needs an offset