In our house, we have a passive hot water recirculating system. It was worked for years, but recently the check valve in the line failed. Two comments: 1) This was a swing type check valve installed on a vertical piece of pipe connected to the output of the water heater and 2) We would, on occasion, see black particles coming from a hot water faucet. As an engineer, I simply don't understand why the valve was installed vertically as I suspect/fear that it never closed and the black particles were flowing up the reticulation line from the water heater.
I got a new swing-type check valve and installed it on a horizontal portion of the piping. While the reciculation function worked properly and the black particles mostly disappeared, regularly the valve would chatter (loudly and annoyingly) because water was trying to flow up the recirculation system when a faucet was opened. I asked about resolving this issue and was told to install a regular check valve.
I did some looking around and settled on a Swagelok B-8C4-1/3 because this valve has the lowest cracking pressure (rated at 1 psi) of any valve I could find. I installed it and 1) the noise went away but 2) the recirculation system may no longer be working (I suspect because there may not enough water pressure to open the valve).
I have two ideas for resolving this issue: 1) find a check valve with an even lower cracking pressure or 2) install the existing valve vertically. My ask of this group is simply this: Which approach should I follow? If replacing the valve, please recommend one.
Thanks.
I got a new swing-type check valve and installed it on a horizontal portion of the piping. While the reciculation function worked properly and the black particles mostly disappeared, regularly the valve would chatter (loudly and annoyingly) because water was trying to flow up the recirculation system when a faucet was opened. I asked about resolving this issue and was told to install a regular check valve.
I did some looking around and settled on a Swagelok B-8C4-1/3 because this valve has the lowest cracking pressure (rated at 1 psi) of any valve I could find. I installed it and 1) the noise went away but 2) the recirculation system may no longer be working (I suspect because there may not enough water pressure to open the valve).
I have two ideas for resolving this issue: 1) find a check valve with an even lower cracking pressure or 2) install the existing valve vertically. My ask of this group is simply this: Which approach should I follow? If replacing the valve, please recommend one.
Thanks.