About a year ago I installed a pressure reducing valve on the water line coming in to the house. The incoming pressure was fluctuating between 80 - 150 pounds. The PRV is now set to 55 pounds.
Water pressure on the outside faucet now reads 55 pounds. I then checked the hot water tank pressure at the drain valve on the tank and it was reading up to 110 pounds after the burner ran.
So I decided to install an expansion tank on the cold line feeding into the water heater. It is a Watts 4.4 gallon tank which I have pre-charged to 55 lbs pressure.
After reading the water tank pressure over a period of several days I am getting pressure readings up to 70 lbs while the burner is running.
Is this normal? I was expecting to see the pressure in the hot water tank to equalize with the 55 lbs set on the expansion tank.
Thank you for any insight!
Water pressure on the outside faucet now reads 55 pounds. I then checked the hot water tank pressure at the drain valve on the tank and it was reading up to 110 pounds after the burner ran.
So I decided to install an expansion tank on the cold line feeding into the water heater. It is a Watts 4.4 gallon tank which I have pre-charged to 55 lbs pressure.
After reading the water tank pressure over a period of several days I am getting pressure readings up to 70 lbs while the burner is running.
Is this normal? I was expecting to see the pressure in the hot water tank to equalize with the 55 lbs set on the expansion tank.
Thank you for any insight!