Have you looked at the NFPA code I referred you to? or at any of the brand water heaters or power vent company's from this country. The Rheem water heater co states to vent safely to the outside, also the Fields co. Stats that it can be used and that it works on a negative draft with proper interlocks to prove draft before the appliance starts. The commonwealth of Massachusetts requires that ALL gas and plumbing products have Product Acceptance through the State Plumbing an Gas board. I feel sorry that you feel that you can't get your point across , and feel like your speaking to complete idiot because YOU have an Engineering degree, but AGAIN this is an APPROVED installation. Please take the time and maybe try to educate yourself on some alternative venting systems that are approved by our National Fuel Code. Again the code is NFPA 54 10.3.4 , Mechanical Draft systems. also 10.3.4.5. The manufacture that I have looked up operate on a negative draft.
Sent from my iPhone using Plumbing Forum
"Hello again Chris",
I did NOT think that I am corresponding with an Idiot at all - as a Plumbing & Gas Inspector I know that You must be very experienced and knowledgeable in these Trades.
In fact having re-read your messages I think that I may have misunderstood what You meant regarding the Installation of a Power Vent `TO` an existing Gas appliance Vent Pipe.
I thought that You meant that a Power Vent Fan could be retrofitted / connected to a Gas Water Heater`s Manufacturers supplied Vent Kit.
I now think that You meant that it could be connected to a constructed Vent Pipe - NOT to a Manufacturers Vent / Flue Kit - although this would still need Manufacturers approval here in the UK and even with Drawings and Calculations submitted the Manufacturers would be very likely to refuse their official approval because of `possible unknown influences` on the Gas Appliance / Ventilation.
As You were so adamant that what You stated is perfectly achievable and `within US / State Gas Safety Codes` I could not understand how there could be such a difference in Gas Safety / Gas Appliance Installation / `Adaptation` Regulations between the UK and the US.
Here in the UK we also have Power Vent systems but they are designed to be retrofitted to chimneys / or Flues / Vent Pipes that have a Gas appliance installed
within a `Fireplace` / Catchment area OR to be installed as a `Designed In` Power Vent / Flue on an appliance Vent / Flue Pipe or on a Multiple appliance Vent / Flue system - with Manufacturers approval obtained for the Vent / Flue Pipe / System design and Installation.
Adapting / connecting to an existing Gas appliance Vent Draft Diverter / Draft Hood and supplied Vent Kit would not satisfy the Manufacturers Installation requirements / Gas Safety Regulations in the UK for retrofitting a Power Vent Fan to the Vent / Flue Pipe.
Also with a Gas appliance that has a Vent Kit / Manufacturers design limitations on the equivalent length of the Vent / Flue Pipe it would obviously NOT be appropriate to install a completely independent Vent / Flue system for either Natural Draught or a Power Vent / Fan Assisted Vent / Flue system.
We cannot discard the Manufacturers Vent Kit / Draught Diverter / Draught Hood OR connect it to a redesigned Vent / Flue Pipe which utilised some of the Manufacturers Vent Pipe Kit - this would be altering the Manufacturers Installation Instructions / Design / Safe Operation criteria.
HERE IS WHAT I THINK YOU MEANT:
You are stating that on an Independent / Constructed Gas Vent / Flue Pipe which is connected to an Atmospheric / Natural Draft Gas Appliance it is permissible in the U.S. / your State to add a Power Vent Fan to that or an adapted Vent pipe and that there would be no concerns about the Safe operation of the Gas appliance - obviously dependant upon the correct installation of the Power Vent Fan / Termination of the Vent and correctly calculated Ventilation for the appliance.
In UK Gas Utilisation / Gas Safety / Manufacturers Design & Installation Instructions for an Appliance that requires a Vent / Flue Pipe to be constructed from the Draft Hood connection to Termination there are obviously some important design criteria / calculations for `Natural Draft` / Atmospheric operation of the Gas appliance / Vent / Flue Pipe and for providing the correct Combustion / Cooling [of location] Ventilation.
In the UK it is definitely NOT permissible to connect a Natural Draft / Atmospheric operated Gas Appliance to a `Power Vented` / Fanned Draft Vent / Flue Pipe without the Manufacturers approval which would be very difficult to obtain or could prove to be very expensive regarding their Engineers Site visits etc.
ANYTHING that is `
Substantially different` to the Manufacturers Installation Instructions / Specifications is classed in the UK as `Immediately Dangerous` and is therefore a breach of the UK Gas Safety Regulations for which Legal action with a possible Prison sentence will follow for the person responsible for the Installation.
With regard to retrofitting `additional Gas Safety Controls` to an appliance - in the past apart from retrofitting a `High Limit Thermostat` / `Overheat Thermostat` supplied by the Manufacturers to some older Gas Boilers [Gas Furnaces] in order to allow them to operate a Sealed Water Central Heating System [with an Expansion vessel] as approved by the Manufacturers there are no `Additional Gas Safety Controls` that are allowed to be retrofitted to a Gas appliance in the UK.
There was a brief period of time when Oxygen Depletion Sensors were supplied by some Manufacturers of Gas Radiant Fires [Open Flue / Vent - Natural Draught] to Gas Engineers for retrofitting on a Service call after some Safety scares about their use in Sleeping accommodation - that was long ago - now ALL Safety Controls are fitted at the point of Manufacture and NOTHING can either be altered or `adapted`.
I had not previously looked at any of the Rheem Gas Water Heaters for use in the U.S. until Tonight - as I expected they are of an Industry Standard design.
If as it does seem that I have misunderstood what You were referring to regarding connecting a Power Vent to an Independent / Constructed Vent / Flue Pipe - Please accept my Apology - having read your replies to Me again I don`t know why this had not become obvious sooner.
My entire sequence of messages on this thread has been influenced by my misunderstanding of what You meant in your original reply to the OP - I am suitably embarrassed !
I am sure that You are a well qualified and experienced Plumbing and Gas Inspector and a credit to your profession.
On this occasion my `Master of Science` Degree in Building Engineering Services and my many Gas Qualifications did not prevent Me from misunderstanding what You meant !
I will probably try to find time to look at the Codes that you identified -just out of Professional interest - But in the past for some reason I have not been able to access specific U.S. Plumbing / Gas Codes via the Internet.