Would like to Check if this is code compliant and can be improved in any way Orting Washington 98360

Plumbing Forums

Help Support Plumbing Forums:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.
The second pic, with the black ABS sewer pipe, looks very wrong. I'll let one of our experts tell you exactly what is wrong, because this is out of my league, but see lots posted here.

The third pic, under the sink, does that black pipe leading upward go to a vent, or another story with plumbing?
 
Your P-trap is backwards. The maximum depth of a P-trap is 4". You probably have more than that with it installed backwards. It's an easy fix. Just cut off the tail piece as required and flip the P-trap around.

1734102613772.png

Also, the second picture of the sanitary tee going to the vent runs horizontal obviously before it reaches 6" above the fixture it is serving. A vent must be vertical or no more than 45 degrees off vertical until it reaches 6" above the flood level of the fixture is serves. And using a sanitary tee there "could" be an issue. Some plumbers and inspectors interpret the plumbing codes to say vents from a horizontal drain line cannot be a sanitary tee but MUST be a combo fitting. I do not hold to that interpretation, but others are absolutely adamant. I will say that should one need to snake down that vent, a combo would make that easier, but other than that, a sanitary tee on its back will vent just fine.

I assume the flow in that picture is from the back to the front. If it is the other way around, that sanitary tee is backwards.

Without knowing the flow directions, fixture locations, pipe sizes, etc., that's about all I can say.
 