WH vent through roof close to parapet wall

Plumbing Forums

Help Support Plumbing Forums:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Gh0st

Member
Joined
Aug 14, 2017
Messages
18
Reaction score
1
Location
,
New Mexico. 20190110_181946.jpg I cant find the part of code that states the distance from parapet wall.i want to say its 3 feet but my problem is i have to be 10 feet from the air intake that puts me up against the parapet wall.
 
parapet.png

looks like if you are closer than 10' / but no closer than 2'

the top of vent has to be 2' above parapet

The above is uniform mechanical code
..................
below is the international mechanical code
#2 shows.....If close to intake be 3' higher that intake


whvent__i_mech_code.png
 
Last edited:

Latest posts

Back
Top